    • dennypageD
      dennypage @lcbbcl
      last edited by

      @lcbbcl I need the messages from the usbhid-ups process. The messages from upsd are expected when usbhid-ups isn't running.

      If you don't have any log entries from usbhid-ups, then please post your ups settings (Services / UPS / Settings)

      I'll be away for a bit... but will look at it when I'm back.

      L 1 Reply Last reply Reply Quote 1
      • L
        lcbbcl @dennypage
        last edited by

        @dennypage
        I have no msg/error from usbhid-ups
        Screenshot_20230220_223805.png

        dennypageD 2 Replies Last reply Reply Quote 1
        • dennypageD
          dennypage @lcbbcl
          last edited by

          @lcbbcl If you re-save your ups settings, it will restart the processes and you should be able to find usbhid entries.

          1 Reply Last reply Reply Quote 1
          • S
            shaffergr @dennypage
            last edited by

            @dennypage

            16:07 removed interruptonly and saved settings

            On console:

            [23.01-RELEASE][X@Y]/root: sysctl kern.corefile=/var/tmp/%N.core
            kern.corefile: /root/%N.core -> /var/tmp/%N.core

            Broadcast Message from root@gw.fubr.org
            (no tty) at 16:07 EST...

            Communications with UPS CyberPower lost

            Broadcast Message from root@gw.fubr.org
            (no tty) at 16:07 EST...

            Communications with UPS CyberPower established

            Feb 20 16:07:40 Y php-fpm[83664]: /nut_settings.php: Stopping service nut
            Feb 20 16:07:40 Y upsmon[66045]: Signal 15: exiting
            Feb 20 16:07:40 Y upsd[97704]: User local-monitor@::1 logged out from UPS [CyberPower]
            Feb 20 16:07:40 Y upsd[97704]: mainloop: Interrupted system call
            Feb 20 16:07:40 Y upsd[97704]: Signal 15: exiting
            Feb 20 16:07:40 Y usbhid-ups[82519]: Signal 15: exiting
            Feb 20 16:07:40 Y php-fpm[83664]: /nut_settings.php: Starting service nut
            Feb 20 16:07:40 Y upsmon[7684]: Startup successful
            Feb 20 16:07:40 Y upsmon[7684]: UPS [CyberPower]: connect failed: Connection failure: Connection refused
            Feb 20 16:07:40 Y upsmon[7684]: Communications with UPS CyberPower lost
            Feb 20 16:07:40 Y usbhid-ups[8439]: Startup successful
            Feb 20 16:07:41 Y upsd[8857]: listening on 192.168.11.1 port 3493
            Feb 20 16:07:41 Y upsd[8857]: listening on ::1 port 3493
            Feb 20 16:07:41 Y upsd[8857]: listening on 127.0.0.1 port 3493
            Feb 20 16:07:41 Y upsd[8857]: Connected to UPS [CyberPower]: usbhid-ups-CyberPower
            Feb 20 16:07:41 Y upsd[8857]: Startup successful
            Feb 20 16:07:45 Y upsd[8857]: User local-monitor@::1 logged into UPS [CyberPower]
            Feb 20 16:07:45 Y upsmon[7684]: Communications with UPS CyberPower established

            Feb 20 17:57:45 Y upsd[8857]: Can't connect to UPS [CyberPower] (usbhid-ups-CyberPower): Connection refused
            Feb 20 17:57:45 Y kernel: pid 8439 (usbhid-ups), jid 0, uid 66: exited on signal 10 (core dumped)
            Feb 20 17:57:48 Y upsmon[7684]: Poll UPS [CyberPower] failed - Driver not connected
            Feb 20 17:57:48 Y upsmon[7684]: Communications with UPS CyberPower lost
            Feb 20 17:57:53 Y upsmon[7684]: Poll UPS [CyberPower] failed - Driver not connected
            Feb 20 17:57:58 Y upsmon[7684]: Poll UPS [CyberPower] failed - Driver not connected

            Also set about 10 minutes later: sysctl kern.sugid_coredump=1

            I have a core dump in /var/tmp/usbhid-ups.core

            What do you want me to do with it?

            dennypageD 1 Reply Last reply Reply Quote 1
            • dennypageD
              dennypage @shaffergr
              last edited by

              @shaffergr said in NUT package:

              I have a core dump in /var/tmp/usbhid-ups.core
              What do you want me to do with it?

              Perfect! Compress and email it to me. Thanks!

              S 1 Reply Last reply Reply Quote 1
              • S
                shaffergr @dennypage
                last edited by

                @dennypage

                email address?

                dennypageD 1 Reply Last reply Reply Quote 1
                • dennypageD
                  dennypage @shaffergr
                  last edited by

                  @shaffergr Sent in chat. Look for a quote bubble next to the pic of your icon at the top. Should have an alert there.

                  S 1 Reply Last reply Reply Quote 1
                  • S
                    shaffergr @dennypage
                    last edited by

                    @dennypage

                    sent via email. Let me know if you don't get it.

                    1 Reply Last reply Reply Quote 1
                    • dennypageD
                      dennypage @lcbbcl
                      last edited by dennypage

                      @lcbbcl I believe I have found what is causing the issue you are experiencing. To correct the issue will require an update to the pfSense nut package as well as updating the underlying FreeBSD nut package used by pfSense. It will take some time.

                      In the interim, you can address the issue by adding the line "user=root" to "Additional configuration lines for ups.conf" under Advanced settings.

                      L keyserK X 3 Replies Last reply Reply Quote 4
                      • L
                        lcbbcl @dennypage
                        last edited by

                        @dennypage
                        Thank you, now is working

                        1 Reply Last reply Reply Quote 1
                        • keyserK
                          keyser Rebel Alliance @dennypage
                          last edited by

                          @dennypage said in NUT package:

                          @lcbbcl I believe I have found what is causing the issue you are experiencing. To correct the issue will require an update to the pfSense nut package as well as updating the underlying FreeBSD nut package used by pfSense. It will take some time.

                          In the interim, you can address the issue by adding the line "user=root" to "Additional configuration lines for ups.conf" under Advanced settings.

                          Your hard and dedicated work on this package is an inspiration. Thank you for the effort :-)

                          I assume it was an access permissions issue since running it as root solves the issue? Can you comment on why it only happens for some UPS models?

                          Love the no fuss of using the official appliances :-)

                          dennypageD 1 Reply Last reply Reply Quote 1
                          • dennypageD
                            dennypage @keyser
                            last edited by

                            @keyser said in NUT package:

                            I assume it was an access permissions issue since running it as root solves the issue? Can you comment on why it only happens for some UPS models?

                            Yes, it's a permissions issue. I am hoping it can be addressed in the FreeBSD nut package (or perhaps in kernel config?), but if not I will have to add the user=root to the config for all usb devices.

                            What models it happens on are dependent upon the quirks defined for that device. If you want to jump down the rabbit hole, run "usbconfig dump_quirk_names" and "usbconfig dump_device_quirks".

                            NB: This is not related to the signal 10/11 issue being experienced with CyberPower units.

                            1 Reply Last reply Reply Quote 3
                            • 4
                              4o4rh
                              last edited by 4o4rh

                              I see the github packages have been moved to

                              https://github.com/pfsense/FreeBSD-ports

                              But i don't see the nut package in there.

                              Where is the code for nut, or is it closed source now?

                              In the upsmon configuration, can we please add two config boxes for the below files.

                              /usr/local/etc/nut/upssched.conf with permission 644
                              /usr/local/bin/upssched-cmd with permission 755

                              To use the scheduler to trigger events from upsmon. these files need to be configurable.
                              Also, there should be a note for using them, the notification box has to be disabled.
                              here is a sample of working files

                              upsmon

                              # upsmon.conf - Configuration for network UPS Tools upsmon
                              # set the path to the notify command processor !!! the UPS notifications option must be unchecked !!! 
                              NOTIFYCMD /usr/local/sbin/upssched
                              
                              # Poll the UPS every 60 seconds.
                              POLLFREQ 60
                              
                              # Wait this many seconds for "Notify Shutdown" messages from slaves
                              POLLFREQALERT 30
                              
                              # time UPS may go missing before being declared dead
                              DEADTIME 600
                              
                              # Warn every 12 hours if battery needs to be replaced
                              RBWARNTIME 43200
                              
                              # Warn every 5 minutes, if UPS is unreachable
                              NOCOMMWARNTIME 300
                              
                              # Messages for the events %s will be replaced with the UPS system identifier in question
                              NOTIFYMSG ONLINE   "UPS %s on line power"
                              NOTIFYMSG ONBATT   "UPS %s on battery"
                              NOTIFYMSG LOWBATT  "UPS %s battery is low"
                              NOTIFYMSG FSD      "UPS %s forced shutdown in progress"
                              NOTIFYMSG COMMOK   "UPS %s communications (re-)established"
                              NOTIFYMSG COMMBAD  "UPS %s communications lost"
                              NOTIFYMSG SHUTDOWN "Auto logout and shutdown proceeding"
                              NOTIFYMSG REPLBATT "UPS %s battery needs to be replaced"
                              NOTIFYMSG NOCOMM   "UPS %s is not reachable"
                              NOTIFYMSG NOPARENT "upsmon parent process died, shutdown impossible"
                              
                              # Change behavior of upsmon on certain events.
                              # Possible values for the flags:
                              # SYSLOG - Write the message in the syslog
                              # WALL - Write the message to all users on the system
                              # EXEC - Execute NOTIFYCMD (see above, in our case see upssched.conf) with the message
                              # IGNORE - Don't do anything
                              # If you use IGNORE, don't use any other flags on the same line.
                              # NOTIFYFLAG <notify type> <flag>[+<flag>][+<flag>] ...
                              NOTIFYFLAG ONLINE   SYSLOG
                              NOTIFYFLAG ONBATT   SYSLOG
                              NOTIFYFLAG LOWBATT  SYSLOG
                              NOTIFYFLAG FSD      SYSLOG+WALL+EXEC
                              NOTIFYFLAG COMMOK   SYSLOG+EXEC
                              NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
                              NOTIFYFLAG SHUTDOWN SYSLOG
                              NOTIFYFLAG REPLBATT SYSLOG
                              NOTIFYFLAG NOCOMM   SYSLOG
                              NOTIFYFLAG NOPARENT SYSLOG
                              

                              upssched

                              # Network UPS Tools - upssched.conf file
                              
                              #Command script to run
                              CMDSCRIPT /usr/local/bin/upssched-cmd
                              
                              # command for pipe and lock files
                              PIPEFN /var/db/nut/upssched.pipe
                              LOCKFN /var/db/nut/upssched.lock
                              
                              # ============================================================================
                              # AT <notifytype> <upsname> <command>
                              # Define a handler for a specific event <notifytype> on UPS <upsname>.
                              # <upsname> can be the special value * to apply this handler to every
                              # possible value of <upsname>.
                              # Run the command <command> via your CMDSCRIPT when it happens.
                              # Note that any AT that matches both the <notifytype> and the <upsname>
                              # for the current event will be used.
                              # ============================================================================
                              # Possible AT commands
                              # - START-TIMER <timername> <interval>
                              #   Start a timer called <timername> that will trigger after <interval>
                              #   seconds, calling your CMDSCRIPT with <timername> as the first
                              #   argument.
                              #   Example:
                              #   Start a timer that'll execute when any UPS (*) has been gone 10 seconds
                              # AT COMMBAD * START-TIMER COMMBAD 1800
                              #   -----------------------------------------------------------------------
                              # - CANCEL-TIMER <timername> [cmd]
                              #   Cancel a running timer called <timername>, if possible. If the timer
                              #   has passed then pass the optional argument <cmd> to CMDSCRIPT.
                              #   Example:
                              #   If a specific UPS (myups@localhost) comes back online, then stop the
                              #   timer before it triggers
                              # AT COMMOK * CANCEL-TIMER COMMBAD COMMOK
                              #   -----------------------------------------------------------------------
                              # - EXECUTE <command>
                              #   Immediately pass <command> as an argument to CMDSCRIPT.
                              #
                              #   Example:
                              #   If any UPS (*) reverts to utility power, then execute
                              #   'ups-back-on-line' via CMDSCRIPT.
                              
                              # UPS is online in syslog. we don't need action when no UPS connected
                              # AT ONLINE * CANCEL-TIMER onbatt 
                              
                              # UPS on battery in syslog. badcomms will shutdown for us
                              # AT ONBATT * START-TIMER onbatt 300
                              
                              # UPS low battery is syslog. we should badcomms to shutdown
                              # AT LOWBATT * START-TIMER lowbatt 300
                              
                              # UPS forced shutdown by master or upsmon
                              AT FSD * EXECUTE powerdown
                              
                              # UPS communications restored
                              AT COMMOK * CANCEL-TIMER badcomms
                              
                              # UPS communications failed. 
                              AT COMMBAD * START-TIMER badcomms 600
                              
                              # UPS shutdown recorded in syslog
                              # AT SHUTDOWN * EXECUTE powerdown
                              
                              # UPS needs replacement battery. Info in syslog
                              # AT REPLBATT * EXECUTE replbatt
                              
                              # UPS is not reachable. Relying on deadtime for shutdown
                              AT NOCOMM * EXECUTE commbad
                              
                              # UPSMON parent process has died - shutdown not possible.
                              # AT NOPARENT * EXECUTE noparent
                              

                              upssched-cmd

                              #! /bin/sh
                              #
                              # This script should be called by upssched via the CMDSCRIPT directive.
                              #
                              # Here is a quick example to show how to handle a bunch of possible
                              # timer names with the help of the case structure.
                              #
                              # This script may be replaced with another program without harm.
                              #
                              # The first argument passed to your CMDSCRIPT is the name of the timer
                              # from your AT lines.
                              #
                              # case $1 in
                              #	upsgone)
                              #		logger -t upssched-cmd "The UPS has been gone for awhile"
                              #		;;
                              #	*)
                              #		logger -t upssched-cmd "Unrecognized command: $1"
                              #		;;
                              # esac
                              
                              case $1 in
                                 onbatt)
                                    # function not needed as we only use syslog
                                    logger -t upssched-cmd "UPS is running on battery."
                                 ;;
                                 
                                 online)
                                    # function not needed as we only use syslog
                                    logger -t upssched-cmd "UPS back online."
                                 ;;
                              
                                 lowbatt)
                                    # function not needed as we only use syslog
                                    logger -t upssched-cmd "UPS has low battery"
                                    # we rely on badcomms when no UPS connected
                                    # /usr/local/sbin/upsmon -c fsd
                                 ;;
                              
                                 badcomms)
                                    logger -t upssched-cmd "UPS offline too long, forced shutdown."
                                    /usr/local/sbin/upsmon -c fsd
                                 ;;
                              
                                 commok)
                                    # function not needed as we only use syslog
                                    logger -t upssched-cmd "UPS communications restored."
                                 ;;
                                 
                                 powerdown)
                                    logger -t upssched-cmd "UPS forced shutdown started"
                                    /usr/local/sbin/upsmon -c fsd
                                 ;;
                              
                                 replbatt)
                                    # function not needed as we only use syslog
                                    logger -t upssched-cmd "UPS battery needs replacing"
                                 ;;
                              
                                 noparent)
                                    # function not needed as we only use syslog
                                    logger -t upssched-cmd "upsmon parent process died. Shutdown not possible"
                                 ;;
                              
                                 *)
                                    logger -t upssched-cmd "No code defined for command: $1"
                                 ;;
                              esac
                              
                              dennypageD 1 Reply Last reply Reply Quote 1
                              • dennypageD
                                dennypage @4o4rh
                                last edited by

                                @gwaitsi It hasn't moved since I wrote it. sysutils/pfSense-pkg-nut.

                                1 Reply Last reply Reply Quote 1
                                • X
                                  xavier1 @dennypage
                                  last edited by

                                  This solved my issue. Everything is working great. Thank you :)

                                  @dennypage said in NUT package:

                                  @lcbbcl I believe I have found what is causing the issue you are experiencing. To correct the issue will require an update to the pfSense nut package as well as updating the underlying FreeBSD nut package used by pfSense. It will take some time.

                                  In the interim, you can address the issue by adding the line "user=root" to "Additional configuration lines for ups.conf" under Advanced settings.

                                  1 Reply Last reply Reply Quote 1
                                  • dennypageD
                                    dennypage
                                    last edited by

                                    @lcbbcl, @xavier1 Would you do me a favor and post the result of

                                    usbconfig -v
                                    

                                    from your systems please? Thanks.

                                    L 1 Reply Last reply Reply Quote 1
                                    • L
                                      lcbbcl @dennypage
                                      last edited by

                                      @dennypage
                                      Here it is

                                      usbconfig -v
                                      ugen0.1: <Intel XHCI root HUB> at usbus0, cfg=0 md=HOST spd=SUPER (5.0Gbps) pwr=SAVE (0mA)
                                      ugen0.1.0: uhub0: <Intel XHCI root HUB, class 9/0, rev 3.00/1.00, addr 1>
                                      
                                       bLength = 0x0012 
                                       bDescriptorType = 0x0001 
                                       bcdUSB = 0x0300 
                                       bDeviceClass = 0x0009  <HUB>
                                       bDeviceSubClass = 0x0000 
                                       bDeviceProtocol = 0x0003 
                                       bMaxPacketSize0 = 0x0009 
                                       idVendor = 0x0000 
                                       idProduct = 0x0000 
                                       bcdDevice = 0x0100 
                                       iManufacturer = 0x0001  <Intel>
                                       iProduct = 0x0002  <XHCI root HUB>
                                       iSerialNumber = 0x0000  <no string>
                                       bNumConfigurations = 0x0001 
                                      
                                      
                                      Configuration index 0
                                      
                                         bLength = 0x0009 
                                         bDescriptorType = 0x0002 
                                         wTotalLength = 0x001f 
                                         bNumInterfaces = 0x0001 
                                         bConfigurationValue = 0x0001 
                                         iConfiguration = 0x0000  <no string>
                                         bmAttributes = 0x0040 
                                         bMaxPower = 0x0000 
                                      
                                         Interface 0
                                           bLength = 0x0009 
                                           bDescriptorType = 0x0004 
                                           bInterfaceNumber = 0x0000 
                                           bAlternateSetting = 0x0000 
                                           bNumEndpoints = 0x0001 
                                           bInterfaceClass = 0x0009  <HUB>
                                           bInterfaceSubClass = 0x0000 
                                           bInterfaceProtocol = 0x0000 
                                           iInterface = 0x0000  <no string>
                                      
                                          Endpoint 0
                                             bLength = 0x0007 
                                             bDescriptorType = 0x0005 
                                             bEndpointAddress = 0x0081  <IN>
                                             bmAttributes = 0x0003  <INTERRUPT>
                                             wMaxPacketSize = 0x0002 
                                             bInterval = 0x00ff 
                                             bRefresh = 0x0000 
                                             bSynchAddress = 0x0000 
                                      
                                           Additional Descriptor
                                      
                                           bLength = 0x06
                                           bDescriptorType = 0x30
                                           bDescriptorSubType = 0x00
                                            RAW dump: 
                                            0x00 | 0x06, 0x30, 0x00, 0x00, 0x00, 0x00
                                      
                                      
                                      
                                      
                                      ugen0.2: <American Power Conversion Smart-UPS C 1000 FW:UPS 12.0 / ID1005> at usbus0, cfg=0 md=HOST spd=FULL (12Mbps) pwr=ON (2mA)
                                      
                                       bLength = 0x0012 
                                       bDescriptorType = 0x0001 
                                       bcdUSB = 0x0200 
                                       bDeviceClass = 0x0000  <Probed by interface class>
                                       bDeviceSubClass = 0x0000 
                                       bDeviceProtocol = 0x0000 
                                       bMaxPacketSize0 = 0x0040 
                                       idVendor = 0x051d 
                                       idProduct = 0x0003 
                                       bcdDevice = 0x0106 
                                       iManufacturer = 0x0001  <American Power Conversion >
                                       iProduct = 0x0002  <Smart-UPS C 1000 FW:UPS 12.0 / ID=1005>
                                       iSerialNumber = 0x0003  <AS1506222288  >
                                       bNumConfigurations = 0x0001 
                                      
                                      
                                      Configuration index 0
                                      
                                         bLength = 0x0009 
                                         bDescriptorType = 0x0002 
                                         wTotalLength = 0x0029 
                                         bNumInterfaces = 0x0001 
                                         bConfigurationValue = 0x0001 
                                         iConfiguration = 0x0000  <no string>
                                         bmAttributes = 0x00e0 
                                         bMaxPower = 0x0001 
                                      
                                         Interface 0
                                           bLength = 0x0009 
                                           bDescriptorType = 0x0004 
                                           bInterfaceNumber = 0x0000 
                                           bAlternateSetting = 0x0000 
                                           bNumEndpoints = 0x0002 
                                           bInterfaceClass = 0x0003  <HID device>
                                           bInterfaceSubClass = 0x0000 
                                           bInterfaceProtocol = 0x0000 
                                           iInterface = 0x0000  <no string>
                                      
                                           Additional Descriptor
                                      
                                           bLength = 0x09
                                           bDescriptorType = 0x21
                                           bDescriptorSubType = 0x00
                                            RAW dump: 
                                            0x00 | 0x09, 0x21, 0x00, 0x01, 0x21, 0x01, 0x22, 0x03, 
                                            0x08 | 0x02
                                      
                                          Endpoint 0
                                             bLength = 0x0007 
                                             bDescriptorType = 0x0005 
                                             bEndpointAddress = 0x0081  <IN>
                                             bmAttributes = 0x0003  <INTERRUPT>
                                             wMaxPacketSize = 0x0040 
                                             bInterval = 0x0014 
                                             bRefresh = 0x0000 
                                             bSynchAddress = 0x0000 
                                      
                                          Endpoint 1
                                             bLength = 0x0007 
                                             bDescriptorType = 0x0005 
                                             bEndpointAddress = 0x0001  <OUT>
                                             bmAttributes = 0x0003  <INTERRUPT>
                                             wMaxPacketSize = 0x0040 
                                             bInterval = 0x000a 
                                             bRefresh = 0x0000 
                                             bSynchAddress = 0x0000 
                                      
                                      1 Reply Last reply Reply Quote 2
                                      • dennypageD
                                        dennypage
                                        last edited by

                                        For those of you affected by the APC issue (and those that will be in the future):

                                        First, I believe that the issue only affects recent APC UPS designs. Those in the last couple of years or so. The core issue is that a new device identification number has been introduced by APC, which FreeBSD is not aware of. Since the kernel does not recognize the device as a UPS that should be ignored, the kernel is attaching an internal driver to it. The presence of this internal driver on the device precludes any non root user from attaching to the device.

                                        This cannot be reasonably fixed in the pfSense nut package or the underlying FreeBSD nut package. The permanent solution requires an adjustment to the usb quirk table in the kernel itself. A patch has been established for the kernel, but I don't know how long it will take to flow through.

                                        In the interim, there are two solutions available:

                                        The first solution, as noted previously, is to add the line

                                        user=root
                                        

                                        to the "Additional configuration lines for ups.conf" section under Advanced settings. This will cause the usbhid-ups command to be run as root. The disadvantage of this approach is that you are running the driver as root, which may be of concern to some.

                                        The alternative solution is to add the line

                                        hw.usb.quirk.0="0x051d 0x0003 0x0000 0xffff UQ_HID_IGNORE"
                                        

                                        to file "/boot/loader.conf.local". Note that you may have to create this file. The disadvantage of this approach is that you will have to reboot pfSense before it will work.
                                        If you previously implemented the user=root approach, you can remove the user=root line following the reboot.

                                        1 Reply Last reply Reply Quote 3
                                        • dennypageD
                                          dennypage
                                          last edited by dennypage

                                          For those of you affected by the CyberPower issue (and those that will be in the future):

                                          First, I want to thank all of you for your help in tracking this down. Particularly @shaffergr, who was kind enough, and trusting enough, to run test builds for me against his CyberPower.

                                          I tracked this down to a double free by the usb code in nut. FWIW, I don’t believe that this issue is completely limited to CyberPower UPSs, but it is probably pretty difficult to encounter with other units as hitting the issue requires a reconnect of the UPS on the bus. CyberPower units are well known to randomly disconnect and reconnect seemingly at random.

                                          For those wondering why this issue did not happen in prior to 23.01: 22.05 and below used nut version 2.7.4. In 2.7.4, nut did not actually close the device when a disconnect happened. Presumably, this may have resulted in a memory leak at shutdown, but I didn’t explore enough to confirm. In 2.8.0, when a device disconnects nut actually closes the device when it disconnects. In fact, it closes it twice on all systems other than Linux. There is even a comment in the code noting how the double close would cause corruption on Linux systems. Unfortunately contrary to the code comments it also causes corruption in FreeBSD.

                                          Having traced this down in the 2.8.0 release code, when I went to the current development version I surprised to find that someone had beat me to it, and fixed the issue back in August. It's just not been release yet. :)

                                          To resolve this will require a new version of nut. Either a new release from the nut team, or for the pfSense team to move from the 2.8.0 release version to the current development version of nut. The nut team is looking toward 2.8.1, but it appears that they have a few things they still want to address before putting that out. I will explore the concept of moving to nut-devel with the pfSense team as time permits (I think they are pretty busy right now). But no matter which way it goes, it’s going to take some time.

                                          In the interim, the only known work-around using the release code (discovered by @tman222) is to add the line

                                          interruptonly
                                          

                                          to the Extra Arguments to driver section. This will cut down some of the information you can see about your UPS, but the important stuff needed to monitor and shutdown should still be there.

                                          Alternatively, if brave souls are interested, I have a build of usbhid-ups made from the FreeBSD nut-devel package. I do not have a CyberPower available so I haven't been able to directly test it, but I expect that it will work.

                                          If you you decide you would like a copy, reach out to me and I will see about getting it to you. For reference, the shasum and sha256sum checksums are:

                                          49ce9131502bfb8b789ee97b7fb3fc81fc9f8fff  usbhid-ups
                                          999a2653559dbc50ecc8ba592a67587b1e307a1495f6e8ebbd3d8e90e3967133  usbhid-ups
                                          
                                          JonathanLeeJ S J W D 5 Replies Last reply Reply Quote 11
                                          • dennypageD
                                            dennypage
                                            last edited by

                                            I'm going to sleep now...

                                            😪

                                            1 Reply Last reply Reply Quote 6