This topic was forked from QNAP recognizing NUT dennypage May 17, 2024, 8:13 PM
This topic has been deleted. Only users with topic management privileges can see it.
  • D
    dennypage @FrankZappa
    last edited by May 20, 2024, 1:28 AM

    @FrankZappa So, your battery date really does show as 2001/09/25. I believe this means that it was not set at the factory. Looks like the apcupsd widget was reporting the UPS manufacture date rather than the battery install date.

    To set the battery date, you can (hopefully) use upsrw.

    Use

    upsrw -l UPSNAME
    

    to see what variables you can write in the UPS. The variable you are looking for is "battery.date".

    Your "ups.test.result" shows that no self test has been run on the UPS. For higher end APC UPSs, this is done by automatic timer. For lower end UPSs, you have to trigger it manually. If you do that, you will have to write the test date yourself--look for variable "ups.test.date" in the upsrw output.

    F 1 Reply Last reply May 20, 2024, 10:07 AM Reply Quote 0
    • D
      dennypage @tgl
      last edited by May 20, 2024, 1:32 AM

      @tgl said in NUT dashboard widget:

      I'm not sure what "battery.date" is really meant to be, but it reads as 2001/09/25 on my APC UPSes too.

      See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

      If the UPS doesn't have time capability, then you are responsible for maintaining this field by hand when you initially install and/or change batteries.

      If your UPS has a network management card, this would be handled automatically. My current APC is like this.

      T 1 Reply Last reply May 20, 2024, 1:36 AM Reply Quote 0
      • D
        dennypage @FrankZappa
        last edited by May 20, 2024, 1:36 AM

        @FrankZappa Forgot to mention. To run a self-test, would use upscmd. To see a list of commands the UPS will accept, use:

        upscmd -l UPSNAME
        

        Most likely, the command will be:

        upscmd UPSNAME test.battery.start
        
        1 Reply Last reply Reply Quote 0
        • T
          tgl @dennypage
          last edited by May 20, 2024, 1:36 AM

          @dennypage said in NUT dashboard widget:

          See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

          On mine, it's not settable period. "upsrw -l" claims to be able to set "battery.mfr.date", but not any other kind of date.

          D 1 Reply Last reply May 20, 2024, 1:37 AM Reply Quote 0
          • D
            dennypage @tgl
            last edited by dennypage May 20, 2024, 1:39 AM May 20, 2024, 1:37 AM

            @tgl What brand/model?

            FWIW, "ups.mfr.date" is a standard field, but I don't recall ever seeing "battery.mfr.date"

            T 1 Reply Last reply May 20, 2024, 1:39 AM Reply Quote 0
            • T
              tgl @dennypage
              last edited by May 20, 2024, 1:39 AM

              @dennypage
              APC Back-UPS Pro BR1500MS2

              D 1 Reply Last reply May 20, 2024, 1:40 AM Reply Quote 0
              • D
                dennypage @tgl
                last edited by May 20, 2024, 1:40 AM

                @tgl Please post Services / UPS / Status.

                T 1 Reply Last reply May 20, 2024, 1:44 AM Reply Quote 0
                • T
                  tgl @dennypage
                  last edited by May 20, 2024, 1:44 AM

                  @dennypage said in NUT dashboard widget:

                  @tgl Please post Services / UPS / Status.

                  I don't actually have NUT installed on my router (yet); this UPS is connected to a Linux server. "upsc" reports what I suppose you want:

                  battery.charge: 100
                  battery.charge.low: 10
                  battery.charge.warning: 50
                  battery.date: 2001/09/25
                  battery.mfr.date: 2022/04/13
                  battery.runtime: 4152
                  battery.runtime.low: 120
                  battery.type: PbAc
                  battery.voltage: 27.3
                  battery.voltage.nominal: 24.0
                  device.mfr: American Power Conversion
                  device.model: Back-UPS RS 1500MS2
                  device.serial: 0B2216N04901  
                  device.type: ups
                  driver.name: usbhid-ups
                  driver.parameter.offdelay: 50
                  driver.parameter.ondelay: 60
                  driver.parameter.pollfreq: 100
                  driver.parameter.pollinterval: 10
                  driver.parameter.port: auto
                  driver.parameter.synchronous: auto
                  driver.version: 2.8.0
                  driver.version.data: APC HID 0.98
                  driver.version.internal: 0.47
                  driver.version.usb: libusb-1.0.23 (API: 0x1000107)
                  input.sensitivity: medium
                  input.transfer.high: 147
                  input.transfer.low: 88
                  input.voltage: 124.0
                  input.voltage.nominal: 120
                  ups.beeper.status: disabled
                  ups.delay.shutdown: 50
                  ups.firmware: 969.e2 .D
                  ups.firmware.aux: e2     
                  ups.load: 10
                  ups.mfr: American Power Conversion
                  ups.mfr.date: 2022/04/13
                  ups.model: Back-UPS RS 1500MS2
                  ups.productid: 0002
                  ups.realpower.nominal: 900
                  ups.serial: 0B2216N04901  
                  ups.status: OL
                  ups.test.result: No test initiated
                  ups.timer.reboot: 0
                  ups.timer.shutdown: -1
                  ups.vendorid: 051d
                  
                  D 1 Reply Last reply May 20, 2024, 2:39 AM Reply Quote 0
                  • D
                    dennypage @tgl
                    last edited by May 20, 2024, 2:39 AM

                    @tgl two quick questions:

                    • Output of upsrw -l
                    • Version of NUT
                    T 1 Reply Last reply May 20, 2024, 2:46 AM Reply Quote 0
                    • T
                      tgl @dennypage
                      last edited by May 20, 2024, 2:46 AM

                      @dennypage

                      Sure:

                      $ upsrw -l xxx_ups
                      [battery.charge.low]
                      Remaining battery level when UPS switches to LB (percent)
                      Type: STRING
                      Maximum length: 10
                      Value: 10
                      
                      [battery.mfr.date]
                      Battery manufacturing date
                      Type: STRING
                      Maximum length: 10
                      Value: 2022/04/13
                      
                      [battery.runtime.low]
                      Remaining battery runtime when UPS switches to LB (seconds)
                      Type: STRING
                      Maximum length: 10
                      Value: 120
                      
                      [input.sensitivity]
                      Input power sensitivity
                      Type: STRING
                      Maximum length: 10
                      Value: medium
                      
                      [input.transfer.high]
                      High voltage transfer point (V)
                      Type: STRING
                      Maximum length: 10
                      Value: 147
                      
                      [input.transfer.low]
                      Low voltage transfer point (V)
                      Type: STRING
                      Maximum length: 10
                      Value: 88
                      
                      [ups.delay.shutdown]
                      Interval to wait after shutdown with delay command (seconds)
                      Type: STRING
                      Maximum length: 10
                      Value: 50
                      
                      

                      The Linux machine is running RHEL8, and its relevant packages are

                      $ rpm -qa | grep ^nut
                      nut-2.8.0-3.el8.x86_64
                      nut-client-2.8.0-3.el8.x86_64
                      $ rpm -qa | grep ^libusb
                      libusb-0.1.5-12.el8.x86_64
                      libusbx-devel-1.0.23-4.el8.x86_64
                      libusbx-1.0.23-4.el8.x86_64
                      libusb-devel-0.1.5-12.el8.x86_64
                      libusbmuxd-1.0.10-9.el8.x86_64
                      
                      D 1 Reply Last reply May 20, 2024, 3:35 PM Reply Quote 0
                      • F
                        FrankZappa @dennypage
                        last edited by May 20, 2024, 10:07 AM

                        @dennypage Hmmmm, tried to change the battery date but was asked for a password. Huh?

                        e3cb8abd-d85c-4a7b-8c65-3f741fd71856-image.png

                        G D 2 Replies Last reply May 20, 2024, 10:30 AM Reply Quote 0
                        • G
                          Gertjan @FrankZappa
                          last edited by May 20, 2024, 10:30 AM

                          @FrankZappa

                          Use the real command line, console or SSH for this - option 8.

                          Start with :

                          cat /usr/local/etc/nut/upsd.users
                          

                          and if all goes well, you see the 'user 'admin, and the password to use.

                          No "help me" PM's please. Use the forum, the community will thank you.
                          Edit : and where are the logs ??

                          1 Reply Last reply Reply Quote 0
                          • D
                            dennypage @FrankZappa
                            last edited by May 20, 2024, 2:47 PM

                            @FrankZappa said in NUT dashboard widget:

                            Hmmmm, tried to change the battery date but was asked for a password. Huh?

                            Yes, writing requires an authorized NUT user. The actual command you will want is:

                            upsrw -s battery.date=2024/05/20 -u admin -p PASSWORD QNAPUPS
                            

                            The admin password is automatically generated when you save the NUT configuration. As @Gertjan notes, you can find the current password in /usr/local/etc/nut/upsd.users.

                            Btw, be sure the date is in the same locale format as upsc outputs.

                            It's easiest to do this all in an ssh session.

                            F 1 Reply Last reply May 20, 2024, 11:16 PM Reply Quote 0
                            • D
                              dennypage @tgl
                              last edited by dennypage May 20, 2024, 3:40 PM May 20, 2024, 3:35 PM

                              @tgl said in NUT dashboard widget:

                              [battery.mfr.date]
                              Battery manufacturing date
                              Type: STRING
                              Maximum length: 10
                              Value: 2022/04/13

                              This looks like a bug in the usbhid-ups driver. The UPS variable being mapped to battery.mfr.date should have been mapped to battery.date. There appear to be other bugs: on my main (new generation) APC, most of the dates and voltages disappear when switching to the USB interface (vs the SNMP interface). I'll dig into this when I have time.

                              Btw, if interested you can find a list of all possible variables here. Variable "battery.date" is defined as "Battery installation or last change date." Variable "battery.mfr.date" is defined as "Battery manufacturing date", and was read-only prior to NUT 8.0.

                              1 Reply Last reply Reply Quote 0
                              • F
                                FrankZappa @dennypage
                                last edited by May 20, 2024, 11:16 PM

                                @dennypage said in NUT dashboard widget:

                                upsrw -s battery.date=2024/05/20 -u admin -p PASSWORD QNAPUPS

                                I tried it with the password and i get the following error "Unexpected response from upsd: ERR READONLY"

                                F 1 Reply Last reply May 20, 2024, 11:21 PM Reply Quote 0
                                • F
                                  FrankZappa @FrankZappa
                                  last edited by May 20, 2024, 11:21 PM

                                  @FrankZappa Also noticed there are two entries in the NUT Services/UPS/Status
                                  battery.date 2001/09/25
                                  battery.mfr.date 2021/04/10

                                  The battery.mfr.date is correct. Thats when I bought the APC.
                                  However, the battery.date (and install date on widget) is waaaaaaay off. Can the widget reflect the battery.mfr.date?

                                  D 1 Reply Last reply May 21, 2024, 7:24 AM Reply Quote 0
                                  • D
                                    dennypage @FrankZappa
                                    last edited by May 21, 2024, 7:24 AM

                                    @FrankZappa said in NUT dashboard widget:

                                    battery.date 2001/09/25
                                    battery.mfr.date 2021/04/10

                                    The battery.mfr.date is correct. Thats when I bought the APC.
                                    However, the battery.date (and install date on widget) is waaaaaaay off. Can the widget reflect the battery.mfr.date?

                                    I've researched a bit, and it appears that the battery date situation with USB UPSs is a bit messed up. In addition to issues like battery.date vs battery.mfr.date you and @tgl encountered with APC, the CyberPower issues appear even worse.

                                    Truth be told, it probably isn't all NUT's fault as it looks like the manufacturers don't seem to completely agree how the dates should map with USB ids.

                                    I think for the time being I'm going to pull the battery install date out of the status widget, at least for USB UPSs. I think as things currently are it would end up causing too much confusion with folks. I'll revisit it in the future.

                                    T 1 Reply Last reply May 21, 2024, 10:02 PM Reply Quote 0
                                    • T
                                      tgl @dennypage
                                      last edited by May 21, 2024, 10:02 PM

                                      @dennypage said in NUT dashboard widget:

                                      I think for the time being I'm going to pull the battery install date out of the status widget, at least for USB UPSs. I think as things currently are it would end up causing too much confusion with folks. I'll revisit it in the future.

                                      Maybe, if the UPS reports both battery.date and battery.mfr.date, you could show the later one?

                                      F D 2 Replies Last reply May 21, 2024, 10:07 PM Reply Quote 0
                                      • F
                                        FrankZappa @tgl
                                        last edited by May 21, 2024, 10:07 PM

                                        @tgl I was thinking the same thing, but didn't want to bug Dennypage anymore. Of course, if Dennypage is bored........well?

                                        1 Reply Last reply Reply Quote 0
                                        • D
                                          dennypage @tgl
                                          last edited by May 21, 2024, 10:51 PM

                                          @tgl said in NUT dashboard widget:

                                          Maybe, if the UPS reports both battery.date and battery.mfr.date, you could show the later one?

                                          Unfortunately, that would be locale specific, which is a real pain for date comparison. I'd rather work on fixing some of the issues with NUT itself.

                                          T 1 Reply Last reply May 21, 2024, 10:59 PM Reply Quote 0