    NUT dashboard widget

    Scheduled Pinned Locked Moved UPS Tools
    43 Posts 5 Posters 4.3k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic was forked from QNAP recognizing NUT dennypage
    This topic has been deleted. Only users with topic management privileges can see it.
    • T
      tgl @dennypage
      last edited by

      @dennypage said in NUT dashboard widget:

      See note above. It just means that it wasn't set at factory or at the point of initial install (which requires a UPS that has time capability).

      On mine, it's not settable period. "upsrw -l" claims to be able to set "battery.mfr.date", but not any other kind of date.

      dennypageD 1 Reply Last reply Reply Quote 0
      • dennypageD
        dennypage @tgl
        last edited by dennypage

        @tgl What brand/model?

        FWIW, "ups.mfr.date" is a standard field, but I don't recall ever seeing "battery.mfr.date"

        T 1 Reply Last reply Reply Quote 0
        • T
          tgl @dennypage
          last edited by

          @dennypage
          APC Back-UPS Pro BR1500MS2

          dennypageD 1 Reply Last reply Reply Quote 0
          • dennypageD
            dennypage @tgl
            last edited by

            @tgl Please post Services / UPS / Status.

            T 1 Reply Last reply Reply Quote 0
            • T
              tgl @dennypage
              last edited by

              @dennypage said in NUT dashboard widget:

              @tgl Please post Services / UPS / Status.

              I don't actually have NUT installed on my router (yet); this UPS is connected to a Linux server. "upsc" reports what I suppose you want:

              battery.charge: 100
              battery.charge.low: 10
              battery.charge.warning: 50
              battery.date: 2001/09/25
              battery.mfr.date: 2022/04/13
              battery.runtime: 4152
              battery.runtime.low: 120
              battery.type: PbAc
              battery.voltage: 27.3
              battery.voltage.nominal: 24.0
              device.mfr: American Power Conversion
              device.model: Back-UPS RS 1500MS2
              device.serial: 0B2216N04901  
              device.type: ups
              driver.name: usbhid-ups
              driver.parameter.offdelay: 50
              driver.parameter.ondelay: 60
              driver.parameter.pollfreq: 100
              driver.parameter.pollinterval: 10
              driver.parameter.port: auto
              driver.parameter.synchronous: auto
              driver.version: 2.8.0
              driver.version.data: APC HID 0.98
              driver.version.internal: 0.47
              driver.version.usb: libusb-1.0.23 (API: 0x1000107)
              input.sensitivity: medium
              input.transfer.high: 147
              input.transfer.low: 88
              input.voltage: 124.0
              input.voltage.nominal: 120
              ups.beeper.status: disabled
              ups.delay.shutdown: 50
              ups.firmware: 969.e2 .D
              ups.firmware.aux: e2     
              ups.load: 10
              ups.mfr: American Power Conversion
              ups.mfr.date: 2022/04/13
              ups.model: Back-UPS RS 1500MS2
              ups.productid: 0002
              ups.realpower.nominal: 900
              ups.serial: 0B2216N04901  
              ups.status: OL
              ups.test.result: No test initiated
              ups.timer.reboot: 0
              ups.timer.shutdown: -1
              ups.vendorid: 051d
              
              dennypageD 1 Reply Last reply Reply Quote 0
              • dennypageD
                dennypage @tgl
                last edited by

                @tgl two quick questions:

                • Output of upsrw -l
                • Version of NUT
                T 1 Reply Last reply Reply Quote 0
                • T
                  tgl @dennypage
                  last edited by

                  @dennypage

                  Sure:

                  $ upsrw -l xxx_ups
                  [battery.charge.low]
                  Remaining battery level when UPS switches to LB (percent)
                  Type: STRING
                  Maximum length: 10
                  Value: 10
                  
                  [battery.mfr.date]
                  Battery manufacturing date
                  Type: STRING
                  Maximum length: 10
                  Value: 2022/04/13
                  
                  [battery.runtime.low]
                  Remaining battery runtime when UPS switches to LB (seconds)
                  Type: STRING
                  Maximum length: 10
                  Value: 120
                  
                  [input.sensitivity]
                  Input power sensitivity
                  Type: STRING
                  Maximum length: 10
                  Value: medium
                  
                  [input.transfer.high]
                  High voltage transfer point (V)
                  Type: STRING
                  Maximum length: 10
                  Value: 147
                  
                  [input.transfer.low]
                  Low voltage transfer point (V)
                  Type: STRING
                  Maximum length: 10
                  Value: 88
                  
                  [ups.delay.shutdown]
                  Interval to wait after shutdown with delay command (seconds)
                  Type: STRING
                  Maximum length: 10
                  Value: 50
                  
                  

                  The Linux machine is running RHEL8, and its relevant packages are

                  $ rpm -qa | grep ^nut
                  nut-2.8.0-3.el8.x86_64
                  nut-client-2.8.0-3.el8.x86_64
                  $ rpm -qa | grep ^libusb
                  libusb-0.1.5-12.el8.x86_64
                  libusbx-devel-1.0.23-4.el8.x86_64
                  libusbx-1.0.23-4.el8.x86_64
                  libusb-devel-0.1.5-12.el8.x86_64
                  libusbmuxd-1.0.10-9.el8.x86_64
                  
                  dennypageD 1 Reply Last reply Reply Quote 0
                  • F
                    FrankZappa @dennypage
                    last edited by

                    @dennypage Hmmmm, tried to change the battery date but was asked for a password. Huh?

                    e3cb8abd-d85c-4a7b-8c65-3f741fd71856-image.png

                    GertjanG dennypageD 2 Replies Last reply Reply Quote 0
                    • GertjanG
                      Gertjan @FrankZappa
                      last edited by

                      @FrankZappa

                      Use the real command line, console or SSH for this - option 8.

                      Start with :

                      cat /usr/local/etc/nut/upsd.users
                      

                      and if all goes well, you see the 'user 'admin, and the password to use.

                      No "help me" PM's please. Use the forum, the community will thank you.
                      Edit : and where are the logs ??

                      1 Reply Last reply Reply Quote 0
                      • dennypageD
                        dennypage @FrankZappa
                        last edited by

                        @FrankZappa said in NUT dashboard widget:

                        Hmmmm, tried to change the battery date but was asked for a password. Huh?

                        Yes, writing requires an authorized NUT user. The actual command you will want is:

                        upsrw -s battery.date=2024/05/20 -u admin -p PASSWORD QNAPUPS
                        

                        The admin password is automatically generated when you save the NUT configuration. As @Gertjan notes, you can find the current password in /usr/local/etc/nut/upsd.users.

                        Btw, be sure the date is in the same locale format as upsc outputs.

                        It's easiest to do this all in an ssh session.

                        F 1 Reply Last reply Reply Quote 0
                        • dennypageD
                          dennypage @tgl
                          last edited by dennypage

                          @tgl said in NUT dashboard widget:

                          [battery.mfr.date]
                          Battery manufacturing date
                          Type: STRING
                          Maximum length: 10
                          Value: 2022/04/13

                          This looks like a bug in the usbhid-ups driver. The UPS variable being mapped to battery.mfr.date should have been mapped to battery.date. There appear to be other bugs: on my main (new generation) APC, most of the dates and voltages disappear when switching to the USB interface (vs the SNMP interface). I'll dig into this when I have time.

                          Btw, if interested you can find a list of all possible variables here. Variable "battery.date" is defined as "Battery installation or last change date." Variable "battery.mfr.date" is defined as "Battery manufacturing date", and was read-only prior to NUT 8.0.

                          1 Reply Last reply Reply Quote 0
                          • F
                            FrankZappa @dennypage
                            last edited by

                            @dennypage said in NUT dashboard widget:

                            upsrw -s battery.date=2024/05/20 -u admin -p PASSWORD QNAPUPS

                            I tried it with the password and i get the following error "Unexpected response from upsd: ERR READONLY"

                            F 1 Reply Last reply Reply Quote 0
                            • F
                              FrankZappa @FrankZappa
                              last edited by

                              @FrankZappa Also noticed there are two entries in the NUT Services/UPS/Status
                              battery.date 2001/09/25
                              battery.mfr.date 2021/04/10

                              The battery.mfr.date is correct. Thats when I bought the APC.
                              However, the battery.date (and install date on widget) is waaaaaaay off. Can the widget reflect the battery.mfr.date?

                              dennypageD 1 Reply Last reply Reply Quote 0
                              • dennypageD
                                dennypage @FrankZappa
                                last edited by

                                @FrankZappa said in NUT dashboard widget:

                                battery.date 2001/09/25
                                battery.mfr.date 2021/04/10

                                The battery.mfr.date is correct. Thats when I bought the APC.
                                However, the battery.date (and install date on widget) is waaaaaaay off. Can the widget reflect the battery.mfr.date?

                                I've researched a bit, and it appears that the battery date situation with USB UPSs is a bit messed up. In addition to issues like battery.date vs battery.mfr.date you and @tgl encountered with APC, the CyberPower issues appear even worse.

                                Truth be told, it probably isn't all NUT's fault as it looks like the manufacturers don't seem to completely agree how the dates should map with USB ids.

                                I think for the time being I'm going to pull the battery install date out of the status widget, at least for USB UPSs. I think as things currently are it would end up causing too much confusion with folks. I'll revisit it in the future.

                                T 1 Reply Last reply Reply Quote 0
                                • T
                                  tgl @dennypage
                                  last edited by

                                  @dennypage said in NUT dashboard widget:

                                  I think for the time being I'm going to pull the battery install date out of the status widget, at least for USB UPSs. I think as things currently are it would end up causing too much confusion with folks. I'll revisit it in the future.

                                  Maybe, if the UPS reports both battery.date and battery.mfr.date, you could show the later one?

                                  F dennypageD 2 Replies Last reply Reply Quote 0
                                  • F
                                    FrankZappa @tgl
                                    last edited by

                                    @tgl I was thinking the same thing, but didn't want to bug Dennypage anymore. Of course, if Dennypage is bored........well?

                                    1 Reply Last reply Reply Quote 0
                                    • dennypageD
                                      dennypage @tgl
                                      last edited by

                                      @tgl said in NUT dashboard widget:

                                      Maybe, if the UPS reports both battery.date and battery.mfr.date, you could show the later one?

                                      Unfortunately, that would be locale specific, which is a real pain for date comparison. I'd rather work on fixing some of the issues with NUT itself.

                                      T 1 Reply Last reply Reply Quote 0
                                      • T
                                        tgl @dennypage
                                        last edited by

                                        @dennypage said in NUT dashboard widget:

                                        Unfortunately, that would be locale specific, which is a real pain for date comparison.

                                        Would it? I'm no expert, but I had the impression that these specific date strings are expected to always have the format yyyy/mm/dd. I agree that it'd be a mess if they don't.

                                        I'd rather work on fixing some of the issues with NUT itself.

                                        Fair, although from what you said upthread it's not clear that that'll yield a solution to this problem.

                                        dennypageD 1 Reply Last reply Reply Quote 0
                                        • dennypageD
                                          dennypage @tgl
                                          last edited by

                                          @tgl said in NUT dashboard widget:

                                          @dennypage said in NUT dashboard widget:

                                          Unfortunately, that would be locale specific, which is a real pain for date comparison.

                                          Would it? I'm no expert, but I had the impression that these specific date strings are expected to always have the format yyyy/mm/dd. I agree that it'd be a mess if they don't.

                                          Yes, the dates are presented in locale specific format. 2024/05/10, 2024/10/05, 05/10/2024, 10/05/2024. My date format is happens to be mm/dd/yyyy (see sample pic above), which I hate. If I had my druthers, all dates would all be in iso format (2025-05-10), but it’s outside of my control.

                                          I'd rather work on fixing some of the issues with NUT itself.

                                          Fair, although from what you said upthread it's not clear that that'll yield a solution to this problem.

                                          I’ve reasonable success working PRs/issues with NUT. Changes need to happen there, because there is no way that the vendors are gonna change anything. 😬

                                          F 1 Reply Last reply Reply Quote 0
                                          • F
                                            FrankZappa @dennypage
                                            last edited by

                                            @dennypage Hi Denny Page,
                                            just curious: Why can't we (you) grab some of the scripting from APCUPSD and add it to the NUT script to produce things like "age of battery" and "power events"? I was able to edit my NUT script to produce the battery install date and changed the text of Vin to Voltage In (see image), but that is the limit of my ability to edit scripts. I'm diving into areas of editing the script that I have zero knowledge of. The APCUPSD was able to calculate the age of the battery, which would be cool to see. Lastly, where in the NUT script does it reach out to get the icon of the green plug you added? Can we have it reference another plug icon? Thanks.

                                            e74c5c82-2535-45a1-8300-ec500c0d3397-image.png

                                            F dennypageD 2 Replies Last reply Reply Quote 0